Wiring in stud wall

Postby jawjaw » Wed Jul 30, 2008 8:36 pm

Please does any wiring run inside a stud wall have to be in a conduit?
Rank: Labourer
Progress to next rank:
Posts: 4
Joined: Mon Apr 14, 2008 8:51 pm


Simply Build It

Postby ericmark » Thu Jul 31, 2008 12:14 am

Although there is special cable designed for stud walls which does not require RCD protection and also using conduit would also allow the non use of RCD's.
The rules with RCD use is new and most wiring in stud walls will be twin and earth.

Postby TOPSPARK » Thu Jul 31, 2008 7:57 pm

Under the 17th edition wiring regulations wiring in stud walls if less than 50mm deep must be protected by a 30 milliamp rcd
Rank: Ganger
Progress to next rank:
Posts: 97
Joined: Fri Jul 25, 2008 9:44 pm

Display posts from previous
Sort by
Order by

  • DIY How to Project Guides

  • DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!