Worried about electric fires


Postby Pothole » Mon Nov 08, 2010 1:20 pm

I have just bought 3 Dimplex Cadiz fires to use in the bedrooms they are rated at 3KW each, I am worried after looking on the web, that my 30amp ring main will not be safe when all are switched on.

pothole
Pothole
Rank: Labourer
Progress to next rank:
0%
Posts: 1
Joined: Mon Nov 08, 2010 12:53 pm

Sponsor

Simply Build It

Postby ericmark » Mon Nov 08, 2010 6:48 pm

If the installation is correct then worst case should be a blown fuse. However we all should have our houses checked every ten years or change of occupant and one of the tests is that the ring main is a ring. If not then one could load up 32A on to wiring only rated at 20A approx.

Also 3Kw is max for 13A plug and if like the kettle the fire only runs for 15 mins then switches off on thermostat then no problems but where the fire is one for hours then the plugs can over heat.

But in real terms the biggest problem with electric fires is items being placed on top of them. After a fire while working for Laing we changed all our convector heaters for oil filled radiators as they were less likely to set paper alight. So easy for draft from door to set papers floating.

Most fires are due to some fault with the fire. Thermostat not working. Or thermal fuse shorted out. And while attended not really a problem.
ericmark
Rank: Project Manager
Posts: 1859
Joined: Fri Oct 02, 2009 8:49 pm
Location: Mold, North Wales.

Display posts from previous
Sort by
Order by



  • DIY How to Project Guides

  • DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!



 