Zone problems


Postby brym » Wed Oct 13, 2010 6:21 pm

Hi, I have a 2 zone system supplied by an oil fuelled boiler. The downstairs zone will only work if the upstairs or hot water systems are running. If I turn on the downstairs separately the boiler and pump come on for about 3 secs then shut down. If the water or upstairs are on the hot water is pumped through the whole system. Each zone has it's own motorised valve and these seem to be working. Help.
brym
Rank: Labourer
Progress to next rank:
25%
Posts: 2
Joined: Wed Oct 13, 2010 6:13 pm

Sponsor

Simply Build It

Postby htg engineer » Thu Oct 14, 2010 7:46 pm

As far as the two zones are concerned, the boiler, pump etc are working - so it has to be the motorised valve or room thermostat on the problem zone at fault.

Assuming it has worked at some point rules out a wiring problem.


htg
htg engineer
Rank: Project Manager
Posts: 3224
Joined: Tue May 22, 2007 5:22 pm

Postby brym » Fri Oct 15, 2010 2:57 pm

Thanks, the room stat seems OK as it switches the boiler on and off when the hot water is also on. I had ruled out the motorised valve as again the radiators warm up when the hot water is on also. Can they jam in a semi open state?

Thanks again for your help.
brym
Rank: Labourer
Progress to next rank:
25%
Posts: 2
Joined: Wed Oct 13, 2010 6:13 pm

Display posts from previous
Sort by
Order by



  • DIY How to Project Guides

  • DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!



 