2 gang mix up
Ask questions and find answers to many subjects relating to electrics and electrical work

4 posts   •   Page 1 of 1
Chubee
Labourer
Labourer
Posts: 1
Joined: Wed Apr 15, 2009 10:43 am

2 gang mix up

by Chubee » Wed Apr 15, 2009 10:50 am

Have moved into a house that was built in the 1970's, decorated and needed to replace the 2G2W switches in the hall and landing.

There are 2 three switches - one at the door (1G1W) for the hall light, one at bottom of stairs for hall and landing and one upstairs for landing and bathroom.

All have three wires (red, blue and yellow). I have tried connecting them back up (the old switches were different at the back) with varying degrees of success.

I thought it was basically suposed to be yellow to common, blue to L1 and red L2 (?) but this gives a avriety of results (eg, hall light will only work if one of switches is in on position).

Any help / ideas please?

kbrownie
Project Manager
Project Manager
Posts: 1995
Joined: Mon Mar 05, 2007 9:36 pm

by kbrownie » Thu Apr 16, 2009 3:16 pm

could be a few different ways of doing this, could you give a clearer description, can't totally understand your post.
it may not been wired correctly in first place.
do your strapper wires (yellow,blue,red) go between switches and then switch wires(red,black) to light
KB

Zap
Labourer
Labourer
Posts: 2
Joined: Sat Apr 18, 2009 3:14 am

RE: 2 GANG MIX UP

by Zap » Wed Apr 22, 2009 12:48 am

As Kbrownie suggests, it is possible that they weren't wired correctly in the first place. However, we have to start somewhere. In each of your 2g2w switch plates, you could expect to see a red and black "twin & earth" cable, and the red, yellow and blue "triple & earth" cable. The twin & earth cables in each switch plate will be supplying the hall and bathroom lights respectively with red to COM and black to L1 of one switch in each switch plate. The red cores are permanently live, and black cores only live with the switch closed. The second switch on each switch plate will be wired to the triple & earth cable for the two way operation of the landing light. Personally, I would follow convention and assume that red cores are those that are normally "permanently live" and thus, these should be connected to the COM terminals. The yellow and blue cores, connected to L1 and L2, will essentially link the two (downstairs and upstairs) switches together. There aren't enough terminals (or space!) in a ceiling rose for a two-way wire up unless supplemented by connector block, which is messy, so most likely, there will be a junction (looping-in) box somewhere inbetween, where the wires going to both switch plates are connected up. The red core (of the triple & earth) going to ONE of the two switch plates, will be connected to the terminal in the junction box to which is connected, the live feed. (referred to as the "permanent live"). The red core of the triple & earth cable going to the other switch plate will only be live when supplied via either the yellow or blue cores depending on switch positioning. This red core (the "switched live"), will be connected to a "separate" terminal in the junction box, along with the brown core from the light fitting flex. The yellow and blue cores will either pass through the junction box unbroken, or be joined (y to y, bl to bl) at their own respective terminals. It is possible, that in the 2g2w switch plate that has the permanent live red for the landing light, a short wire link exists between both COM terminals, which will provide the permanent live to the other switch rather than via the red core of a separate twin & earth cable.
Long-winded I know, and possibly not a match for your situation but hopefully will give you some inspiration!?

bd3cc
Foreman
Foreman
Posts: 323
Joined: Wed Jan 30, 2008 8:02 pm

by bd3cc » Fri May 01, 2009 10:57 pm

I would sugest if you only have 3 wires, red to common, and the other 2 in L1/L2 doesnt matter which way round, assuming this is 2 way switching.