Cold Radiator

Post by davidtate73 » Wed Nov 05, 2008 6:19 pm

Hi
This my first posting and would like some help I have a sealed system boiler and the down stairs radiator only gets hot at the top half this is the only radiator with no stat valves can someone tell me how to get the radiator hot all the way down I had to top the system up as it had shut down last week

plumbbob
Project Manager
Project Manager
Posts: 1892
Joined: Wed May 07, 2008 9:59 pm

Post by plumbbob » Thu Nov 06, 2008 6:53 pm

Hot at the top and not at the bottom indicates poor flow of hot water. Try balancing the system. For help, check the projects section of this site and search for article on how to balance a heating system.

Steve the gas
Site Agent
Site Agent
Posts: 780
Joined: Sun May 04, 2008 7:07 am

Post by Steve the gas » Fri Nov 07, 2008 5:31 am

Hi David,

Could be sludge build up,but, I would try balancing the rads first before anything else and bleeding of course (with heating off of course)

Hth

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 5:22 pm

Post by htg engineer » Fri Nov 07, 2008 2:28 pm

If balancing doesn't work, turn off both valves and remove the problem radiator, you will be able to tell by the colour/quality of the water whether or not you have a sludge problem.

Htg