CONSUMER UNIT

by DEAN WHITTINGTON » Mon Sep 28, 2009 4:30 pm

I HAVE A DUAL RCD CONSUMER UNIT WITH 1 X 80A (30MA) AND 1 X 63A (30MA) RCD'S
I CAN PUT 2 X 40A SHOWER MCB'S PLUS A 32A MAINS CCT MCB ON THE 80A RCD BUT IF I TRANSFER ANY OF THEM TO THE 63A RCD THEY TRIP BOTH THE RCDS .
THE ONLY MCB'S I CAN USE ON THE 63A RCB ARE THE 6A LIGHT CTTS

WHAT AM I DOING WRONG.

kbrownie
Project Manager
Project Manager
Posts: 1995
Joined: Mon Mar 05, 2007 9:36 pm

by kbrownie » Mon Sep 28, 2009 7:36 pm

what are you doing with the neutrals?

sparx
Project Manager
Project Manager
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.

by sparx » Mon Sep 28, 2009 8:37 pm

hi ,not transfering the neutrals to the correct half?
you have 2 neutral bars & whichever rcd you put a circuit L in the corresponding neutral MUST go on the same N side.

DEAN WHITTINGTON
Labourer
Labourer
Posts: 3
Joined: Mon Sep 28, 2009 3:33 pm

CONSUMER BOX

by DEAN WHITTINGTON » Wed Sep 30, 2009 8:55 am

THANKS FOR YOUR GREAT HELP AND QUICK REPLIES
PROBLEM FIXED IN TEN MINUETS
THANK AGAIN