Postby Bogart » Sun Jan 19, 2020 5:31 pm

Am about to install two ovens, one above the other. Both are rated at 16A max. Now am wondering about the feed and isolation needs, here are my alternatives, in my opinion.

1 Feed both off a 32A MCB using 2.5mm2 and a single 32A isolation switch by the ovens in the kitchen

2 As above but use 2 seperate 20A switches in the kitchen

3 Feed each oven seperately using 16A MCB x 2 and fed by a 4C 1.5mm2 cable

Opinions gratefully received.
Bogart
Rank: Apprentice
Progress to next rank:
15.8%
Posts: 8
Joined: Fri Oct 25, 2019 9:48 am


Sponsor

Simply Build It

Postby ericmark » Mon Jan 20, 2020 4:30 am

Odd but this question has been asked on another forum when the oven supplier refused to connect them up.

I motor needs a local isolator, but an oven or hob does not, the isolator could be anywhere including with a TN supply using the MCB or RCBO.

All it needs is a method to lock it off.

However most ovens and hobs have around 1.5 meters of flex which needs connecting to the supply, so you do need a cooker connection unit to actually change from fixed house wiring to flexible cable going to oven or hob.

As to size of supply, I would say 32A is normal and having one 32A supply for both is OK, however 45A is not normal and I would not directly connect a 45A supply to an oven, unless the manufacture says it is permitted.

Clearly two 16A supplies is best option, but that is not normally done, you can get double cooker connection units designed to connect two cables into the supply, I would use one of them.

If the ovens are British and 3 kW or less I would use two fuse connection units, if using non British and it is over 3 kW then just use a double cooker connection unit.

Personally I would use a 45A isolator on the wall so you can local isolate so there are no problems in the future if you want a supplier to connect up a new oven, as they often want to be able to see the isolator, but it is not required, just good practice.
ericmark
Rank: Project Manager
Posts: 2390
Joined: Fri Oct 02, 2009 8:49 pm
Location: Llanfair Caereinion, Mid Wales.


Postby Bogart » Tue Jan 21, 2020 9:07 am

Am not sure why you state a cooker connection unit is required. T&E into a DP switch then flexible out to the oven.
Bogart
Rank: Apprentice
Progress to next rank:
15.8%
Posts: 8
Joined: Fri Oct 25, 2019 9:48 am


Postby ericmark » Thu Jan 23, 2020 1:45 pm

Reason for cooker connection unit is to have some where to connect the oven within 1.5 meters of the oven, other wise some cooker supply people will not connect it.

Does not really matter if a dedicated cooker connection unit, or a switch but some thing within 1.5 meters of the oven or cooker.

In this case two ovens so between them it would need a 32A supply, so a cooker isolation switch would be required for that current. I know you can get a light switch rated 20A but I would not be happy with 20A switch on a 32A supply.
ericmark
Rank: Project Manager
Posts: 2390
Joined: Fri Oct 02, 2009 8:49 pm
Location: Llanfair Caereinion, Mid Wales.


Postby Bogart » Fri Jan 24, 2020 10:12 am

I would be splitting the ovens so each cable from the splitting point only needs 16A capability so a 20A switch is fine.
Bogart
Rank: Apprentice
Progress to next rank:
15.8%
Posts: 8
Joined: Fri Oct 25, 2019 9:48 am



Display posts from previous
Sort by
Order by



  • DIY How to Project Guides
  • DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!


 