The system has been in service for 10 yrs now and to my knowledge has never been flushed out. The system is working ok but having recently taken a radiator off the wall to paper behind it, found that the water that came out of the radiator was really quite black. I just assumed from this that it needed a clean out.
many thanks for replying
if it's black water and not thick black sludge, then there's no need for a powerflush (saves alot of money).
You can either remove all radiators and flush outside with a hose pipe. Then all you have is the pipework to drain and refill a few times until the water is clear.
or
Add a system cleanser, leave in for the recommended time, drain whole system, refill and drain until water runs clear.
Either way the only way to completely remove all the rubbish is to remove all downstairs radiators (Upstairs will empty when drained from somewhere downstairs) downstairs radiators will remain full unless the pipes feeding the radiators come up from the floor and there's a drain point below the floor.
Once you have the whole system filled with fresh water, don't forget to add inhibitor, if this is added and replenished everytime the system is drained, it'll probably never need flushing again.
htg
Last edited by htg engineer on Tue Jul 28, 2009 8:17 pm, edited 2 times in total.
Many thanks for the advice. it is black water and not sludge so I will not have to power flush.
I will add a system cleanser and do it that way.
Many thanks for the advice.
DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!