Light Fitting Electrics and Mass of Wires

Postby mountainmj » Sun Apr 05, 2020 9:54 am

I have just gone to change a light fitting. After opening it up I have found a whole mess of wires. The previous light fitting was a 3 way spot light and I want to replace it for a standard hanging light.

I was just going to take the live, neutral, and earth wires and switch them to the new fitting but as I was doing this a few of the connectors had come loose and fell off and now I have a whole load of wires and I don't know how to connect them.

I have attached a photo of what I am left with. I've numbered the wires from 1 to 7

    1 - Earth - 2 naked wires going from the earth wire to the grey wires where 2 and 3; and 6 and 7 come from
    2 - Black
    3 - Red
    4 - Red - At the top of 4 and 5 there is a naked wire also coming out of the main grey wire
    5 - Brown coming out of a black - At the top of 4 and 5 there is a naked wire also coming out of the main grey wire
    6 - Black
    7 - Red

The first picture is of the old fitting. The second is the new fitting. The third is the connectors that fell off. And the fourth picture is the wires coming from the ceiling.

Could someone please tell me how I should connect these up? My gut feeling is that the 3 red wires (3,4,7) should be joined together and go to the live connection on the light fitting, the 3 black wires should be connected together and go to the neutral connection on the light fitting and the 3 naked wires should be connected together and insulted and then go to the earth on the light fitting.

Many thanks in advance for any advice given.
Attachments
IMG_20200405_100947-min-min.jpg
old fitting
IMG_20200405_100932-min-min.jpg
new fitting
IMG_20200405_100909-min-min.jpg
connectors that fell off
IMG_20200405_100843-min-min.jpg
Wires coming from ceiling. At the top of 4 and 5 there is a naked wire that connects to nothing
mountainmj
Rank: Apprentice
Progress to next rank:
0%
Posts: 5
Joined: Mon Jun 17, 2019 7:05 am


Sponsor

Simply Build It

Postby Mr White » Sun Apr 05, 2020 8:47 pm

If you did as you suggest (All reds together and all blacks together) It will go BANG!

What you have is quite normal (It's called the 3 plate system)
You have:
One supply cable
One to the next light cable
One to the switch cable

The 3 reds should be connected together, but NOT connected to the light.
TWO of the blacks should be connected together and to the neutral of the light. The remaining black goes to the LIVE of the light (It is the switched live)

The 3 bare wires should be sleeved and all connected to the earth.

The question is which two blacks should be connected together, without being able to test, the answer is no idea. But as I said get it wrong and it will go BANG. Does one of the blacks have red tape or sleeving on it? if it does it is the other two blacks you connect together.
Mr White
Rank: Site Agent
Progress to next rank:
39%
Posts: 695
Joined: Tue Jun 20, 2017 9:54 pm


Postby mountainmj » Sun Apr 05, 2020 9:24 pm

Thank you. I figured it out. It all works as expected now. Cheers
mountainmj
Rank: Apprentice
Progress to next rank:
0%
Posts: 5
Joined: Mon Jun 17, 2019 7:05 am



Display posts from previous
Sort by
Order by



  • DIY How to Project Guides
  • DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!


 