Postby poosemon » Sat Nov 02, 2019 4:03 pm

Quick ceiling light wiring question. 1st point to make is I have made the rookie error of dismantling everything before fitting as thought it would be a like for like, however I do see to have the arrangement mentioned in a lot of postings.

However, I can’t seem to quite find an answer of how to wire into my particular light fitting (B & Q so assume it must be a fairly common standard?)

Existing Wiring;
2x Red
2x Black (of which one has a red sleeve on so assume it is the switched one)
2x Yellow and Green.

New Light Fitting:
3 Terminals only;
L – Manual states Red (or brown)
Earth – Green/Yellow
N – Blue and Black

Any advice would be gratefully received.
poosemon
Rank: Labourer
Progress to next rank:
0%
Posts: 1
Joined: Sat Nov 02, 2019 3:58 pm


Sponsor

Simply Build It

Postby chriscba » Sat Nov 02, 2019 10:28 pm

I take you are replacing a pendant locket drop.

The 2 reds will have to put in a chock block as this is the loop to the next light.

The black with red sleeve is the switch wire, this goes to L.

The black goes to N.

The earths green & yellow go to E.
chriscba
Rank: Ganger
Progress to next rank:
18.7%
Posts: 78
Joined: Thu Aug 27, 2009 10:00 pm


Postby Mr White » Sun Nov 03, 2019 12:09 am

You need extra terminal block or wago connectors for the two reds.
Your assumption regarding the black with the red sleeve is correct.
Mr White
Rank: Site Agent
Progress to next rank:
5.6%
Posts: 528
Joined: Tue Jun 20, 2017 9:54 pm



Display posts from previous
Sort by
Order by



  • DIY How to Project Guides
  • DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!


 