no hot water - is it the valve

by biffaman1 » Tue Aug 14, 2007 9:40 am

I've got no hot water, C/H OK. Tank stat has been changed, and is OK. The H/W valve is a honeywell one, and I've opened it manually to let water through to no avail. I've taken the motor out, and manually turned the spindle, but still no luck. Can the valve become separated in the pipe from the spndle, so even if you turn it by hand it's still closed?
The valve is a V4043H

Its an indirect system, and it appears that the boiler is not being called for H/W when you press the button on the programmer.

thanks

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 6:22 pm

by htg engineer » Tue Aug 14, 2007 9:07 pm

The spindle could of snapped inside the body, but would be very rare as there's not enough force from the actuator head to do this. The spindle will only turn quarter of a turn to change from heating to water and heating, so check you haven't turned this too much.

If you hold the pipe A outlet, this is for heating, then turn the valve to see when pipe from port B becomes hot. This will be heating the water.