Poor circulation, boiler cutting out

Post by en7gjh » Tue Feb 26, 2008 7:46 pm

Hello, please help me.

The symptons are as follows:
The boiler tends to run for about a minute and then cut out for 30 seconds, while the pump continues running. The pump is making a horrendous noise that doesn't sound normal, which can be heard throughout the house from each of the radiators (resonance, vibration etc).

The pipes either side of the pump are boiling to touch (hotter than any normal radiator, about 80 deg C), along with the inlet pipes for most radiators and the top of each radiator, but not the bottom or outlet pipe.
Radiators are hotter upstairs than downstairs (boiler and pump are upstairs).

When the boiler cuts out is does so with a kettling sound like the water is boiling inside, the F&E pipe is scalding and the water in the tank warm (in attic).

This problem went away for a while and has come back again, when I suddenly closed a TRV (sudden increas in flow rate on pump affecting impellor?).

Is the pump working just not at 100%, therefore not moving the water around fast enough, causing the boiler to cut out due to low flow rate (expanding into F&E tank), and not being able to heat all radiators??

Please help

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 5:22 pm

Post by htg engineer » Thu Feb 28, 2008 5:27 pm

Sounds like a problem with the pump, the inpeller may have broken or may be loose. I would strip off pump head and check impeller. replace pump if needed.

en7gjh
Apprentice
Apprentice
Posts: 5
Joined: Tue Feb 26, 2008 7:36 pm

Post by en7gjh » Thu Feb 28, 2008 6:24 pm

I tried to replace the pump but struggles to remove the gate valve from the pump. As this involved draining the system, because I removed the gate valve from the pipe work, the pump appears to sound a bit better.
I now can not get the pilot to stay alight!!!!

Any thoughts?

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 5:22 pm

Post by htg engineer » Thu Feb 28, 2008 7:53 pm

What's the make and model of the boiler ?

if the boiler is over-heating it could be the over-heat stat keeping the pilot off.

en7gjh
Apprentice
Apprentice
Posts: 5
Joined: Tue Feb 26, 2008 7:36 pm

Post by en7gjh » Thu Feb 28, 2008 8:35 pm

It is a Thorn Apollo. The pilot not staying alight has only happened since I took the pump out and drained the system earlier today. Pilot hasn't gone out once during all my troubles with the boiler cutting out.

I really am grateful for the advice provided, thank you.

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 5:22 pm

Post by htg engineer » Thu Feb 28, 2008 9:24 pm

The Apollo does have an overheat stat, if you drained the boiler - when you filled it, air may have became trapped in the heat-ex. If this happened then the overheat stat would cut the pilot out.

Check the thermocouple does it have an interrupter ? electrical leads connected to the 2 spades.

If it's an apollo fanfare - do not under any circumstances remove the combustion chamber cover unless you are 100% sure how to put it back on. As they have a positive pressure case - a family was killed in my area a few year back, where an Apollo Fanfare case was not fitted properly.

If you cant get it to light - it's probably best to get a heating engineer in to repair, temporarily bridging the overheat stat with a screwdriver or similar sometimes gets the pilot going.

en7gjh
Apprentice
Apprentice
Posts: 5
Joined: Tue Feb 26, 2008 7:36 pm

Post by en7gjh » Thu Feb 28, 2008 11:30 pm

Thanks. Why would the overheat stat cut out the pilot if i can not get it to stay alight, not really generating any heat?

what are the 2 spades?

Cheers

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 5:22 pm

Post by htg engineer » Fri Feb 29, 2008 12:00 pm

The overheat stat will cut the pilot out if the boiler overheats, with you draining the boiler i'm guessing that is what happened, when you turned the boiler on after re-filling there may have been sir stuck in the boiler or pump - if the boiler didn't get rid of the heat quick enough - it would cut the pilot out. It could still be the overheat stat keeping the pilot from re-lighting.

But could also just be a dirty pilot or thermocouple needs replacing.

Get a engineer out to repair.

en7gjh
Apprentice
Apprentice
Posts: 5
Joined: Tue Feb 26, 2008 7:36 pm

Post by en7gjh » Fri Feb 29, 2008 7:34 pm

Just cleaned the thermocouple - no joy, I will get a replacement tomorrow.

It is now stone cold asa not been used for 24 hours, bled both pump and boiler (not that that is relevant if the pilot won't stay alight on its own).

Let you know how i get on. Will a screwfix thermocouple be compatibile with Thorn Apollo 30/50?