pressure loss

Post by gary10 » Mon Feb 25, 2008 3:59 pm

i have a halstead quattro combi boiler in the loft that keeps loosing pressure but every time i re pressurize the system water comes out of the overflow pipe outside can anyone advise please

ALDA
Foreman
Foreman
Posts: 397
Joined: Mon Feb 04, 2008 8:15 pm

Post by ALDA » Mon Feb 25, 2008 5:03 pm

FAULTY PRESSURE RELIEF VALVE

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 5:22 pm

Post by htg engineer » Mon Feb 25, 2008 6:56 pm

It could be and sounds like a fault with the pressure relief valve,

What have you been taking the pressure to ?

the Presssure relief valve will normally open between 3.0 and 4.0 bar. If it's leaking outside - at 1.0 - 1.5 bar then replace the PRV and all should work fine.