I am replacing a Danfos old style electro-mechanical Programmer type 103 with a Salus EP100 Single Channel Programmer but am a bit unsure about the wiring.
There is a room Thermostat fitted to the system but am not sure how you wire this on the Salus EP100.
mountainman1952,
You will have difficulty with your proposal. The Danfos is used to switch two circuits - hot water which supplies power to fire the boiler and central heating which powers the pump usually via a room stat.
The salus can only switch one circuit so will not replace the danfos.
end
According to the User Manual for the Danfos 103 "Your 103 timeswitch has one time output which can be used to control your heating and hot water at the same times". This is why I bought a single channel programmer to replace it. The wiring diagram in the manual also only shows one output. Have I got the wrong manual for the Danfos?
mountainman1952,
Yes you are correct I was picturing the rectangular controller with separate settings for ch and hw.
Terminal 2 on the danfoss becomes live when the controller is calling for heat. There may be two wires connected to this terminal.
You should end up with neutral and live on the N and L terminals and the wires to terminal 2 on the danfos should be connected onto terminal 3 of the Salus. Terminals 1, 2 and 4 are unused.
end
DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!