Postby robinjon » Sat Oct 17, 2020 12:42 pm

I recently connected a spur direct to my consumer unit. Reason was it was a simple back-to-back job through the wall to make an outdoor socket. Internal connection was via the 'sockets' circuit and to an approved, modern 'outdoor weatherproof socket. All connected smoothly.
Except that when I tried to use the socket, the rcb tripped. Is it possible to use a spur like this or must spurs come from a 'circuit'? Alternatively, does this reaction indicate a cable fault?
Any thoughts or suggestions gratefully received.
robinjon
Rank: Labourer
Progress to next rank:
50%
Posts: 3
Joined: Sat Oct 17, 2020 11:57 am


Sponsor

Simply Build It

Postby Mr White » Sat Oct 17, 2020 8:50 pm

When you say "you connected a spur directly to your consumers unit" what exactly did you connect it to?

(Pictures also help)
Mr White
Rank: Site Agent
Progress to next rank:
54.2%
Posts: 771
Joined: Tue Jun 20, 2017 9:54 pm


Postby ericmark » Sun Oct 18, 2020 7:28 am

[img]https://www.consumerunitworld.co.uk/ekmps/shops/consumer/resources/Design/inside-high-integrity-consumer-unit.jpg[/img]I hope the picture works, it shows 1/2/3 : (Three) Neutral Bars - the defining feature of a High Integrity Consumer Unit 4: Earth Bar.

The RCD works by comparing supply and return, if the same it will not trip, other wise it trips, likely you have selected wrong neutral bar, or if using RCBO's wrong trip for neutral.
ericmark
Rank: Project Manager
Posts: 2440
Joined: Fri Oct 02, 2009 8:49 pm
Location: Llanfair Caereinion, Mid Wales.


Postby ericmark » Sun Oct 18, 2020 7:32 am

[attachment=0]inside-high-integrity-consumer-unit.jpg[/attachment]May be this will work better? it shows 1/2/3 : (Three) Neutral Bars - the defining feature of a High Integrity Consumer Unit 4: Earth Bar.

Wrong neutral bar and it will trip.
Attachments
inside-high-integrity-consumer-unit.jpg
ericmark
Rank: Project Manager
Posts: 2440
Joined: Fri Oct 02, 2009 8:49 pm
Location: Llanfair Caereinion, Mid Wales.


Postby robinjon » Mon Oct 19, 2020 3:18 pm

Many thanks for your responses guys. Mr white - it was connected to the 'Socket Ground floor' circuit.

Ericmark - you were absolutely right. I wasn't even aware that there were different Neutral banks on a CU. anyway the problem is now sorted and everything is working as it I intended it should. Thanks again.

Robinjon
robinjon
Rank: Labourer
Progress to next rank:
50%
Posts: 3
Joined: Sat Oct 17, 2020 11:57 am



Display posts from previous
Sort by
Order by



  • DIY How to Project Guides
  • DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!


 