Voltage drop on cable for a borehole type pump

by James71 » Tue May 19, 2020 9:41 am

I’m installing a borehole type pump around 150m from the generator it will be powered by. The pump is rated at .55kW so 4mm armoured cable should do the job accommodating the voltage drop. however pumps like this have a power spike of around 3.5x when they start up - how does this affect 5e calculation? Do I need to size the cable for 2kW?

ericmark
Project Manager
Project Manager
Posts: 2850
Joined: Fri Oct 02, 2009 9:49 pm
Location: Llanfair Caereinion, Mid Wales.

Re: Voltage drop on cable for a borehole type pump

by ericmark » Thu May 21, 2020 6:13 am

I make volt drop at 10 amp to be around 14.6 volts, i.e. the start current, and I would not expect there to be a problem.

James71
Labourer
Labourer
Posts: 2
Joined: Tue May 19, 2020 9:26 am

Re: Voltage drop on cable for a borehole type pump

by James71 » Thu May 21, 2020 7:07 pm

ericmark wrote:I make volt drop at 10 amp to be around 14.6 volts, i.e. the start current, and I would not expect there to be a problem.


Lovely, thanks