Whats this valve for??

by plotnine » Sun Sep 14, 2008 2:14 pm

I have a simple fully pumped CH and HW system. The flow from the pump connects to the two zone valves from a tee connection. The controller allows for separate function of the zone valves so it is possible to have just hot water, just central heating, or both depending on timer settings.

I also have one gate valve which I can’t not see the reason for.

After the pump and before the tee to the zone valve there is a tee. This feeds to a gate valve that is just cracked open, the outlet connects to the downstream side of the HW water zone valve via another tee.

This valve is allowing the hot water to bypass the HW zone valve even when only CH is called for.

Any ideas why the corgie plumber who installed the system would have fitted it? Is it really necessary and how can I regulate the setting to prevent hot water heating when I don’t want it.

plumbbob
Project Manager
Project Manager
Posts: 1892
Joined: Wed May 07, 2008 10:59 pm

by plumbbob » Sun Sep 14, 2008 9:31 pm

The valve is called a bypass, and ensures a continual flow of water around the boiler circuit if both motorised valves are shut. This is fitted to protect the pump and boiler. As you say, this valve should be just open enough to ensure a flow, any further, and the hot water would not be pumped around the heating circuit.

plotnine
Labourer
Labourer
Posts: 3
Joined: Sun Sep 14, 2008 2:06 pm

by plotnine » Sun Sep 14, 2008 10:39 pm

Thanks plumbbob.

Do you agree that this valve should be connected into the circuit after the pump and return liv e from the cylinder and hot watertank, not as it is currently jusat bypassing the hotwater zone valve?

plotnine

plumbbob
Project Manager
Project Manager
Posts: 1892
Joined: Wed May 07, 2008 10:59 pm

by plumbbob » Mon Sep 15, 2008 5:01 pm

Yes, I would normally expect the bypass to do exactly that; bypass the heating circuits not just the valves, otherwise the water will as you say, be heated even when the m/v is closed.

It may be worthwhile you just checking the plumbing again, taking particular note of the pump direction. It just seems strange someone should go to the trouble of fitting a bypass, and then go and fit it in the wrong place.

Are you sure the gate valve is not in series with the dhw circuit? This would be expected if a restrictor valve was fitted. Such a valve would only be partially open and is fitted to limit the flow through the cylinder coil forcing the remaining hot water around the heating circuit (if called for).

plotnine
Labourer
Labourer
Posts: 3
Joined: Sun Sep 14, 2008 2:06 pm

by plotnine » Tue Sep 16, 2008 4:23 pm

Hello Bob,

The pump flow definatey goes TO the tee which feeds the HW and CH zone valves. The gate valve is definately in parallel not series with the HW zone valve................I guess the plumber got it wrong.

I am happy that i have interpreted the circuit correctly, I was in Hydraulics all my working life so am used to sorting out other peoples systems.

Anyway thanks , you do seem to agree with me that its in the wrong place, I am past playing with spanners myself so i will find a reliable plumber, who speaks English, and get him to correct it for me. Thanks again

David