Wiring for a 11Kw Electric Boiler

Post by notadiyer » Sun Apr 13, 2008 12:12 am

Hi
I want to know from you in the know if I can join two existing 6mm cables (to make 12mm) as I want to fit a 11kw electric boiler as there are two 6mm supplies running through the loft, surface clipped to roof joists, (neatly may I say) that have never been connected as they were originally installed by the previous owner for provision of two en-suite electric showers but were never used as they decided to have plumbed in showers installed. They are both terminated into the CU onto seperate MCB's on the RCCB protected side.
Installing 10mm cable would be a real (decoritve wise) job. Total length of run is approx. 12/14 metres, about 5 of which are burried in the plastered wall upto the loft.

Look forward to answers from the experts out there who can advise the best way to do this, if allowed?

Thanks

ericmark

Post by ericmark » Sun Apr 13, 2008 2:40 pm

Appendix 10 of BS7671:2008 (17th Edition) covers parallel conductors full of do’s and don’t and calculations. Basically you must ensure neither cable can become over loaded. So in general must be of equal length and size. 11kw is 47.8 amps and 6mm² cable clipped to wooden joist etc with no more than 100mm insulation is method 100 from table 4A2 so rated at 34 amp table 4D5 but how does it get to loft space if through insulated stud wall pushed down through centre then we move to method 103 and then 6mm² drops to 23.5 amp put two together then rating factor of something like 0.8 so down to 18.8 amp per cable giving 37.6 amp for pair and I haven’t started on air temperatures. But it become apparent you must know the route the cables take as although they could be big enough for use in loft space you have not said how they get there. If all the way buried in plaster or loft then should be OK. At 7.3mV/A/m and 14 meters two cables only 2.5 volts volt drop so that’s OK but each cable will only be approx 0.1Ω each and any slight variation could cause one cable to overload using two MCB’s will ensure if one does overload it will trip out, but the MCB’s have resistance and could be the cause of imbalance, so I would tend to use one, but use a clamp on ammeter on first use to check balance which needs to be within 10%. The regulations start at 433.4 Overload protection of conductors in parallel. Out of interest I put the figures you give into my excel program to select cable sizes and it selects 16mm² not 10mm² at 46 amp selects 10mm² so two 6mm² cables would be better than 10mm² and since I only list up to 16mm² in look-up tables if insulation is over 100mm or if in centre of stud wall methods 101 and 103 it fails. I look at regulation 433.1.1 and I read this as saying 1.45 times the lowest of the current-carrying capacity of each cable so 49.3amp with method 100 so 50 amp MCB would seem to fit the bill. Although I realise you may not be able to read the 17th Edition wiring regulations we give the regulations so anyone else reading my reply can verify in case I have miss read one. I would use the two existing cables after being satisfied the route was OK but would include in my installation certificate the clip on ammeter reading as well as the earth loop impedance etc. This way in the future electricians can compare readings when checking for any bad connections. Prospective short circuit current between line and neutral is also important as electricians may not have a clip on ammeter but will have psc meter when doing the 10 year or change of ownership inspection and tests. Since the circuits are already there it is possible you will not need Part P but I recommend you follow links and read yourself as sorting out latter can as we have seen on here be quite a problem.

sparx
Project Manager
Project Manager
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.

Post by sparx » Sun Apr 13, 2008 9:22 pm

Hi,
Eric has as ever done a good job of researching possible problems.
Personally I read it that the run from C.U. goes straight up wall in plaster to loft then surface 'clipped direct' to original shower positions.
As long as the 2 cables run together along all the way AND they are fed from a single Circuit Breaker NOT 2 seperate ones I would go with it.
Presuming the cables end up at different points at the moment then at least one of them will have to be rerouted to be next to the other one, and if this leaves one short then I would fit an isolator at the point of the shortest cable if near where heater is going and then run on to heater with a length of 10mm2. This will negate the need to find a way of joining these large cables in an approved manner.
hope this helps,
SPARX