baxi 105e help pressure loss

Postby manicmag17 » Sun Dec 05, 2010 8:23 am

hi all, new to tis so please bare with me...recently replaced the blank on pressure release valve,far as i no it a common fault and it the second time i done this,,but since doing this the boiler not keeping its pressure, as far as i no there no leaks, any ideas all help welcome thanks
Rank: Labourer
Progress to next rank:
Posts: 1
Joined: Sun Dec 05, 2010 8:10 am


Simply Build It

Postby htg engineer » Sun Dec 05, 2010 7:24 pm

What blank ?

There should be no water coming from pressure relief valve, pressure should be 1.0 - 1.5 bar when cold. When hot the pressure shouldn't rise above 3 bar, combi fill should be dis-connected and blanked.

If you're losing pressure, there's either a leak, the pressure relief valve is passing, the diaphragm in the pressure vessel is split (if pressure rises to above 3 bar, when system hot) or the combi fill is on/passing - overfilling system will open pressure relief valve.

htg engineer
Rank: Project Manager
Posts: 3224
Joined: Tue May 22, 2007 5:22 pm

Display posts from previous
Sort by
Order by

  • DIY How to Project Guides

  • DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!