BAXI SOLO 30 PROBLEM

by sreno66 » Sun Apr 13, 2008 10:48 am

FITTED SOLO 30 FILLED SYSTEM, FIRED UP FOR TEN MINS AND THEN SHUT DOWN CANNOT GET BOILER TO FIRE BACK UP. ANY SUGGESTIONS PLEASE. I KNOW PROBLEM WITH AIR TRIED LINKING DRY SENSOR BUT STILL NOTHING...

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 6:22 pm

by htg engineer » Sun Apr 13, 2008 11:40 am

CORGI registered ?

if not get an installer in to put right and check boiler has been fitted correctly and legally.

sreno66
Labourer
Labourer
Posts: 3
Joined: Sun Apr 13, 2008 10:07 am

CORGI?

by sreno66 » Mon Apr 14, 2008 9:46 pm

YES. I HAVE BEEN REGISTERED FOR OVER TEN YEARS.

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 6:22 pm

by htg engineer » Wed Apr 16, 2008 11:32 am

Are there any manual resets that may be keeping the boiler off ?
over heat stat
flue over heat
etc ?

If not what does happen ?
Pump runs - fan runs - air pressure switch proven - ignition

sreno66
Labourer
Labourer
Posts: 3
Joined: Sun Apr 13, 2008 10:07 am

TANKS FOR REPLY

by sreno66 » Wed Apr 16, 2008 5:26 pm

[quote="htg engineer"]Are there any manual resets that may be keeping the boiler off ?
over heat stat
flue over heat
etc ?

If not what does happen ?
Pump runs - fan runs - air pressure switch proven - ignition[/quote]

Baxi went to job yesterday and found that the pc board was faulty, thanks for replying.