c/heating system drained + refilled now not working


Postby dscott@live.co.uk » Tue Jun 12, 2012 8:28 pm

Hi there,
i was changing a radiator in the bathroom and drained the system as i needed to move pipes and change valves etc but in the middle of doing this someone flicked the heating on in the house while the system was drained and now the radiators in the house arent heating.the hot water is fine but the boiler is only coming on for a short time then cutting out.the water pump seems fine as its vibrating as normal but no heat to rads.can anyone help? its an oil boiler with an open vented heating system????
dscott@live.co.uk
Posts: 1
Joined: Tue Jun 12, 2012 8:15 pm

Sponsor

Simply Build It

Postby plumbbob » Wed Jun 13, 2012 7:51 pm

If the hot water is fine, then the most logical explanation is the system is airlocked. Switch the system to CH only and switch on. Check in the airing cupboard to make sure you have not missed any bleed valves.

If you live in a bungalow and the pipes are in the loft, check up there as there are often valves sticking up in the loft.
plumbbob
Posts: 1853
Joined: Wed May 07, 2008 9:59 pm


Postby htg engineer » Sat Aug 11, 2012 7:31 am

If you're having problems clearing the airlock, try draining down again and refilling.
htg engineer
Posts: 3193