    cable rating on a spur?



    neweysonline.co.uk - The newest tool of the trade




    Post a reply




    4 posts • Page 1 of 1

    cable rating on a spur?

    Postby skin » Sat Aug 30, 2008 10:58 pm

    hi all
    as a practising part p electrician, i needed clarification on a issue i have regarding double sockets that are on a spur off a ring main socket... the rules state that the number of spurs are limited to one off each socket on a ring. what would happen if you plugged in 2 3kw heaters into that spur socket? as this spur is on a single 2.5 cable which is only rated at about 19 amps. the current that the 2 heaters would draw would be 26 amps. now the mcb will not trip but the cable will overheat and surely melt and maybe catch fire. how can you cover yourself from this kind of possibilty? maybe use 4mm cable?
    thanks for reading
    skin
     
    Posts: 12
    Joined: Fri Jun 01, 2007 1:07 am
    Top

    Re: cable rating on a spur?

    Postby BLAKEY1963 » Sun Aug 31, 2008 12:31 pm

    [quote="skin"]hi all
    as a practising part p electrician, i needed clarification on a issue i have regarding double sockets that are on a spur off a ring main socket... the rules state that the number of spurs are limited to one off each socket on a ring. what would happen if you plugged in 2 3kw heaters into that spur socket? as this spur is on a single 2.5 cable which is only rated at about 19 amps. the current that the 2 heaters would draw would be 26 amps. now the mcb will not trip but the cable will overheat and surely melt and maybe catch fire. how can you cover yourself from this kind of possibilty? maybe use 4mm cable?
    thanks for reading[/quote]

    SKIN
    The easiest way to protect the 2.5 mm2 cable against overloaded
    appliances , if the twin socket is used for the spur is to
    fit next to it a fused spur unit , so a maximum load of only 13amps
    can be drawn


    BLAKEY1963
    BLAKEY1963
     
    Posts: 655
    Joined: Wed Jun 13, 2007 10:57 pm
    Top

    Postby mephistico » Sun Aug 31, 2008 1:48 pm

    It one of those anomalies of the regs. You have to take diversity into account. What are the chances of someone using a 26A load on a double socket?
    Your argument is perfectly sound but if you have ever calculated the maximum demand on a house it comes out at 160A (typical) and your service fuse is 60 or 80A.
    It based on not everything been used at the same time.
    mephistico
     
    Posts: 10
    Joined: Sun Aug 31, 2008 6:23 am
    Top

    Postby ericmark » Sun Aug 31, 2008 2:29 pm

    Hi Skin nice to see a thinking man.
    You are of course correct you could draw 26 amp and 2.5mm² 70°C flat twin and earth is rated between 13.5 and 27 amp. Reading Appendix 15 it seems 2.5mm² to BS6004
    Electric cables. PVC insulated, non-armoured cables for voltages up to and including 450/750 V, for electric power, lighting and internal wiring Insulated cables, Polyvinyl chloride, Sheathed cables, Electric cables, Power cables, Single-core cables, Multicore cables, Electric conductors, Cable sheaths, Cable cores, Lighting systems, Electrical properties of materials, Mechanical properties of mat

    However 90°C is up to 33 amp clipped direct either as twin and earth or Ali-Tube and the latter complies with BS 8436.

    So
    1) Twin and earth could be OK for 26 amp if cable installed correct.
    2) Reading IET forum seems double sockets are only rated to 20A.
    3) And there are 2.5mm² cables able to handle the extra current.
    4) It is very unlikely that two items taking 13 amp for any length of time will ever be used in the same pair of sockets.
    Therefore it is not completely against the rules but very much on the edge.


    Eric
    ericmark
     
    Top


    Post a reply

    4 posts • Page 1 of 1

    Return to Electrics





     


    • { RELATED_TOPICS }
      Replies
      Views
      Last post
    • ring cable rating/mcb rating
      by aido » Sun Jun 24, 2007 7:48 pm
      3 Replies
      1583 Views
      Last post by aido View the latest post
      Wed Jun 27, 2007 7:52 pm
    • Rating for Ali-tube cable
      by ericmark » Mon Sep 15, 2008 9:01 pm
      0 Replies
      565 Views
      Last post by ericmark View the latest post
      Mon Sep 15, 2008 9:01 pm
    • Cable rating re: Wiring Matters
      by ericmark » Wed Nov 25, 2009 2:58 pm
      3 Replies
      1619 Views
      Last post by ericmark View the latest post
      Thu Nov 26, 2009 9:35 pm
    • How far can a spur cable run?
      by Bob Foale » Sun Dec 16, 2007 10:48 pm
      1 Replies
      1288 Views
      Last post by sparx View the latest post
      Mon Dec 17, 2007 5:20 pm
    • Spur cable length
      by kev85 » Mon May 14, 2007 2:28 pm
      1 Replies
      1038 Views
      Last post by sparx View the latest post
      Mon May 14, 2007 8:04 pm

    • Board index
    • The team • Delete all board cookies • All times are UTC
    • SitemapIndex SitemapIndex
    • RSS Feed RSS Feed
    • Channel list Channel list
    Powered by phpBB® Forum Software © phpBB Group
    cron





    Diy Doctor Ltd  (Company No. 5863375)

    DIY  |  DIY How To  |  DIY Forum  |  Terms & Conditions  |  Privacy Policy  |  Cookie Info  

    © Copyright DIY Doctor Ltd 2011  Developed by Boson Media  Hosted by Rackspace