Cold Water Tank Problem
All aspects of plumbing questions and answers, help, tips and information

4 posts   •   Page 1 of 1
dazer
Labourer
Labourer
Posts: 1
Joined: Tue Jun 02, 2009 8:37 pm

Cold Water Tank Problem

by dazer » Tue Jun 02, 2009 8:40 pm

Hope someone can help with this - for the last 2 days my cold water tank in the attic has not been automatically refilling. I cannot easily reach the tank so what I did was just hit the side with a broomhandle and immediately the water started going in.

Does this sound like the float is touching the side of the tank and sticking? It has been unusually hot over the last 2 days and i wonder if heat expansion is causing the float and tank side to touch?

thanks

stoneyboy
Project Manager
Project Manager
Posts: 6418
Joined: Wed Dec 10, 2008 6:44 pm

by stoneyboy » Thu Jun 04, 2009 11:17 pm

dazer,
Replace the ball valve complete and don't forget to flush out the pipe before fitting the new valve.
end

Steve the gas
Site Agent
Site Agent
Posts: 780
Joined: Sun May 04, 2008 8:07 am

by Steve the gas » Fri Jun 05, 2009 6:37 am

Hi,

Service or change the valve.

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 6:22 pm

by htg engineer » Fri Jun 05, 2009 2:50 pm

You need to check the float and valve, it's sometimes easier to replace the valve rather than trying to repair, it may just be the float or the valve may be sticking also - pretty straight forward job if you can overcome the access problem.


htg

4 posts   •   Page 1 of 1
It is currently Wed Mar 27, 2024 6:29 am