combi boiler--dhw return
All aspects of plumbing questions and answers, help, tips and information

2 posts   •   Page 1 of 1
james woodland
Labourer
Labourer
Posts: 1
Joined: Sun Sep 07, 2008 12:01 pm

combi boiler--dhw return

by james woodland » Sun Sep 07, 2008 3:12 pm

I have a 35meter pumped D.H.W run, I installed a return but there is no connection to the floor standing combi boiler, can I drop it into the c/f (mains)

many thanks james

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 6:22 pm

by htg engineer » Tue Sep 09, 2008 6:44 pm

Combi boiler with pumped hot water ?

Water should not be pumped directly from the mains, you can only pump water from a storage tank.

'I installed a return but there is no connection to the floor standing combi boiler'

So where does the return go to now ?
Why do you think you need/want a return ? the pump will only come on when the tap is opened, so should only pump the water used.

The only reason to fit a pump with a return is if you have a continuous loop, where each feed to a tap is tee'd into the main distribution pipe, used in hospitals where there's long runs and you need instant hot water, not long lags of cold water.


htg

2 posts   •   Page 1 of 1
It is currently Wed Apr 03, 2024 8:10 am