Postby james woodland » Sun Sep 07, 2008 2:12 pm

I have a 35meter pumped D.H.W run, I installed a return but there is no connection to the floor standing combi boiler, can I drop it into the c/f (mains)

many thanks james
james woodland
Posts: 1
Joined: Sun Sep 07, 2008 11:01 am

Sponsor

Simply Build It

Postby htg engineer » Tue Sep 09, 2008 5:44 pm

Combi boiler with pumped hot water ?

Water should not be pumped directly from the mains, you can only pump water from a storage tank.

'I installed a return but there is no connection to the floor standing combi boiler'

So where does the return go to now ?
Why do you think you need/want a return ? the pump will only come on when the tap is opened, so should only pump the water used.

The only reason to fit a pump with a return is if you have a continuous loop, where each feed to a tap is tee'd into the main distribution pipe, used in hospitals where there's long runs and you need instant hot water, not long lags of cold water.


htg
htg engineer
Posts: 3193
Joined: Tue May 22, 2007 5:22 pm