Combi boiler pressure falls to zero when heating is put on


Postby monkay » Thu Nov 11, 2010 5:26 pm

Hi,
I just went to turn the heating on and it is not working. The pressure is reading just under 0.5 bar and when I put the heating on the pressure falls to 0.

I've got the instruction manual but it doesn't say how to increase pressure only how to decrease it.

Could someone give some help which tap I need to turn to increase pressure please?

There only seems to be a tap on the DHW inlet but I have turned and turned this and nothing happens.
monkay
Rank: Labourer
Progress to next rank:
0%
Posts: 1
Joined: Thu Nov 11, 2010 5:13 pm

Sponsor

Simply Build It

Postby frank pope » Wed Nov 17, 2010 1:42 pm

Check under the boiler and locate the cold water supply pipe (15mm), there will be a valve located in the pipe (flexi-hose) or on the boiler nearby. Open the inlet and you will hear water entering the system. Monitor the guage to 1 to 1.5 bar. You may need to bleed the radiators after repressurising (heating off) as there may be air in the system causing a loss of pressure.
frank pope
Rank: Apprentice
Progress to next rank:
5.3%
Posts: 6
Joined: Thu May 17, 2007 1:51 pm

Display posts from previous
Sort by
Order by



  • DIY How to Project Guides

  • DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!



 