Danfoss 103 to Drayton LP111 for Potterton Boiler


Postby dyce1984 » Thu Jun 15, 2017 4:41 pm

currently trying to swap the danfoss for the drayton and its not happening
the boiler is a potterton combi and there is a thermostat in the hallway I've tried to interpret the drayton instructions using the corresponding terminals for the danfoss ...
there is a 4 core coming from the boiler live/neutral and black connected to the stat then to term 2 of the drayton also a blue connected to the stat and then to terminal 6 of the drayton

what I have at the moment is the stat controlling the boiler at all times and the drayton seemingly not involved at all ...
pulling my hair out
dyce1984
Rank: Labourer
Progress to next rank:
0%
Posts: 1
Joined: Thu Jun 15, 2017 4:23 pm

Sponsor

Simply Build It

Postby ericmark » Sat Jun 17, 2017 4:19 am

Line in Danfoss 6 Drayton L
Neutral Danfoss 5 Drayton N

The Line may be linked Danfoss 3 Drayton 1 or you could have volt free connection.
To boiler Danfoss 1 Drayton 3

I would guess there is a link wire and you have missed moving that across.
ericmark
Rank: Project Manager
Posts: 1796
Joined: Fri Oct 02, 2009 8:49 pm
Location: Mold, North Wales.

Display posts from previous
Sort by
Order by



  • DIY How to Project Guides

  • DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!



 