Earthing kitchen sink/boiler?


Postby worm » Tue Oct 07, 2008 4:21 pm

What size cable is usual or the minimum requirement for earthing the kitchen sink?

Does the boiler 'combi' Glow worm also need earthing?

thanks
worm
Rank: Apprentice
Progress to next rank:
84.2%
Posts: 21
Joined: Wed Oct 03, 2007 9:36 am

Sponsor

Simply Build It

Postby john9159 » Wed Oct 08, 2008 6:12 pm

From the mains service head you need to run 10 mm sq green/yellow sheathed conductors. On all the other supplementary bonding you would use 6 mm sq green/yellow sheathed conductors.
Yes, assuming your boiler has electrical connections within you will earth this.
Refer to DIY Doctor info at:
http://www.diydoctor.org.uk/projects/bo ... throom.htm
john9159
Rank: Ganger
Progress to next rank:
6%
Posts: 59
Joined: Sun Nov 25, 2007 4:56 pm

Postby ericmark » Wed Oct 08, 2008 9:51 pm

I would have said 4mm but today I was told there is no need to earth a sink.
Also not need to add any extra earths to a combi other than that which is part of power supply.
The sink may need an earth if metal waist is used.
Eric
ericmark

Display posts from previous
Sort by
Order by



  • DIY How to Project Guides

  • DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!



 