Flow Pipe Hotter Than Radiator on Radiator Furthest From Boiler


Postby Nick56789 » Sun Jan 04, 2015 7:42 pm

Hello

The radiator that is furthest from my boiler struggles to heat up to the temperatures of the other radiators. I use an infrared thermometer to measure the temperatures and it is consistently 10 degrees cooler than the others.

The flow pipe is fitted with a two-way TRV. As I type the room thermostat is calling for heat, the boiler is on, the flow pipe on this radiator is 55 degrees Celcius, while the hottest part of the radiator is 44 degrees C. The TRV is set to 5, its highest setting. The lockshield valve is fully open.

Is this symptomatic of a blocked TRV?

Thanks
Nick56789
Rank: Apprentice
Progress to next rank:
0%
Posts: 5
Joined: Sat Sep 27, 2014 9:59 am

Sponsor

Simply Build It

Postby htg engineer » Sun Jan 04, 2015 8:23 pm

No, the TRV controls the temperature of the room not the radiator.

Water will always take the easiest route, the furthest radiator has more restrictions in pipework. Try closing the lockshield valves on all pother radiators then only open them up 2/3 turns. The restricted flow through these will increase the flow to the problem radiator.
htg engineer
Rank: Project Manager
Posts: 3224
Joined: Tue May 22, 2007 5:22 pm

Display posts from previous
Sort by
Order by



  • DIY How to Project Guides

  • DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!



 


  • Related Topics