help with boiler asap please


Postby bazza » Tue Oct 02, 2007 8:34 pm

hi guys fitted an external expansion vessel on a baxi 105e but now wen i put the heating on the bar pressure on the gauge dosnt move it stays at 1 bar then after about 5 mins the boiler main burner goes out i teed the vessel into the return pipe close to the boiler wat hav i dun wrong n shud i fit a external prv n seperate warning pipe need advise as quick as possible THANX 4 any advise bazza
bazza
Rank: Ganger
Progress to next rank:
79.3%
Posts: 169
Joined: Mon May 14, 2007 4:40 pm

Sponsor

Simply Build It

Postby htg engineer » Wed Oct 03, 2007 3:54 pm

Check automatic airvent is open.

Do the temperature lights go up to 70degrees ?

Does the flow pipe from the boiler get hot. and do the radiators heat up ?

Did you turn off the flow and return isolation valves ? are they fully open ?
and have you vented all radiators, pump ?
htg engineer
Rank: Project Manager
Posts: 3224
Joined: Tue May 22, 2007 5:22 pm

Postby bazza » Mon Oct 08, 2007 10:32 am

thanx 4 advise you were right the automatic air vent had bin closed off so i opened it n after a bit of rumblin it seems 2 be workin fine now ps sorry 4 late reply bin really busy cheers bazza
bazza
Rank: Ganger
Progress to next rank:
79.3%
Posts: 169
Joined: Mon May 14, 2007 4:40 pm

Display posts from previous
Sort by
Order by



  • DIY How to Project Guides

  • DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!



 