MAxi Boiler
7 posts   •   Page 1 of 1
Milpol1
MAxi Boiler
by Milpol1 » Wed Jul 21, 2010 8:16 pm
I have a Baxi Boiler and the problem is that when I turn the control knob to "water only"" the boiler does not fireevery time to heat the water,furthermore if it does fire it takes an extriordinary while to heat the water, however, if I turn the knob to"Heating and Water the boiler fires up as normal. Any ideas would be greatly received and thanks in advance.
eggers
by eggers » Fri Jul 23, 2010 6:27 pm
suggests to me some kind of valve fault. i assume you do not have a combi boiler.
Is the system an "s-plan" system, with 2 or more zone valves? Under that circumstance i think you will find the hot water valve is not bringing the boiler on, but with heating on the heating valve does bring the boiler on, and as the hot water valve is already open, you are heating the tank aswell.
If it's a combi boiler, chances are the diverter valve is at fault, which boiler do u have?
Milpol1
Boiler
by Milpol1 » Sun Jul 25, 2010 4:08 pm
Its a Baxi Combi Model 80 e
by htg engineer » Sun Jul 25, 2010 10:20 pm
Diaphragm in Pressure Differential will be split or stretched, replacing this will solve the intermittent hot water fault.
htg
Milpol1
by Milpol1 » Mon Jul 26, 2010 6:42 pm
[quote="htg engineer"]Diaphragm in Pressure Differential will be split or stretched, replacing this will solve the intermittent hot water fault.
htg[/quote]
eggers
by eggers » Mon Jul 26, 2010 9:39 pm
diaphram is split, 20 min job to fix for anyone gas safe registered
Eva2100
reply
by Eva2100 » Wed Aug 04, 2010 10:24 am
thank for sharing your advice..