Oven Wiring


Postby pg29 » Fri Jun 15, 2007 9:45 pm

Can anyone advise, I recently submitted a post about a similer problem. I have a 4mm twin+earth feed from a 32A Breaker to the kitchen Oven. I am getting a new kitchen designed with 2 ovens and would like to use this supply to feed my 2 Ovens 1 oven @2.8Kw and the other @ 7.2Kw Can i use the 4mm feed to a consumer panel then fuse them independently or does each oven in a new installation need to be wired dirctly from the main fuse board. Is the wiring rated sufficient, Also does any one know if i have to install a new 10mm earth cable to a new stainless steel sink or can i connect it using the current earth cable in the kitchen (2.5 or 4mm )
pg29
Rank: Apprentice
Progress to next rank:
5.3%
Posts: 6
Joined: Mon Jun 11, 2007 2:57 am

Sponsor

Simply Build It

Postby BLAKEY1963 » Sat Jun 16, 2007 12:37 am

[quote="pg29"]Can anyone advise, I recently submitted a post about a similer problem. I have a 4mm twin+earth feed from a 32A Breaker to the kitchen Oven. I am getting a new kitchen designed with 2 ovens and would like to use this supply to feed my 2 Ovens 1 oven @2.8Kw and the other @ 7.2Kw Can i use the 4mm feed to a consumer panel then fuse them independently or does each oven in a new installation need to be wired dirctly from the main fuse board. Is the wiring rated sufficient, Also does any one know if i have to install a new 10mm earth cable to a new stainless steel sink or can i connect it using the current earth cable in the kitchen (2.5 or 4mm )[/quote]
PG29
THIS WORK IS NOTIFIABLE AND NEEDS TO BE CARRIED OUT BY A REGISTERED CONTRACTER.
THE 4 MM2 IF INSPECTED AND TESTED AND SAFE TO REMAIN IN SERVICE COULD BE UTILISED TO FEED THE 2.8 KW OVEN AND THE 32 AMP PROTECTIVE DEVICE CHANGED TO A 16 AMP MCB.
PERSONALLY I WOULD WIRE A 6MM2 CABLE FOR THE 7.2 KW OVEN , AND UTILISE THE 32 AMP MCB , FOR THE NEW CIRCUIT .
YOU WOULD RUN A 10 MM2 EARTH TO THE SINK UNIT AS A SUPPLEMENTARY BONDING CONDUCTOR IF EARTH LOOP IMPEADANCES
IN CIRCUITS FEEDING APPLIANCES IN THE KITCHEN COULD NOT BE MET. THIS WOULD BE EVALUATED BY YOUR REGISTERED ELECTRCIAN.
4 MM2 CAN BE USED FOR SUPPLEMENTARY BONDING BUT AGAIN YOUR ELECTRICIAN WOULD DECIDE ON THE BONDING REQUIREMENTS AFTER
LOOKING AT YOUR PLUMBING AND PIPE WORK.

BLAKEY1963

BLAKEY1963
BLAKEY1963
Rank: Site Agent
Progress to next rank:
31.6%
Posts: 658
Joined: Wed Jun 13, 2007 10:57 pm

Postby pg29 » Sat Jun 16, 2007 6:58 pm

thanx very much,
pg29
Rank: Apprentice
Progress to next rank:
5.3%
Posts: 6
Joined: Mon Jun 11, 2007 2:57 am

Display posts from previous
Sort by
Order by



  • DIY How to Project Guides

  • DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!



 