Plastering over cables


Postby greg-s » Fri Feb 13, 2009 9:24 pm

Hi, I'd be glad for your advice please on whether cable can be plastered over directly or does it have to run under a protective cover or tubing. In this case it's a spur using 2.5mm to a socket. The cable length is 2mts. Thanks - good to have found this site.
greg-s
Rank: Labourer
Progress to next rank:
25%
Posts: 2
Joined: Fri Feb 13, 2009 9:13 pm

Sponsor

Simply Build It

Postby kbrownie » Sat Feb 14, 2009 11:03 am

HI greg-s,
They can be plastered straight over with out any mechancical protection, providing the cables are routed within the permited areas.
If they are not routed within these area they need to be buried at least 50mm in to wall surface (that includes both side of a partition wall) or have mechanical protection.
It is advisable to protect the cable though from damage that the plasterers trowel may cause, so not a requirment but a good idea.
KB
kbrownie
Rank: Project Manager
Posts: 1993
Joined: Mon Mar 05, 2007 9:36 pm

Postby rosebery » Sat Feb 14, 2009 11:10 am

It should be mechanically protected (capping or oval conduit). Capping protects it from the clumsy spread and his sharp trowel (:lol:). If you use conduit then the cable can be easily replaced if necessary later or another cable added if necessary and if the conduit is large enough.

KB is correct in that there is no actual requirement not to plaster over directly. I would argue that it's not good practice though.
Last edited by rosebery on Sat Feb 14, 2009 8:55 pm, edited 1 time in total.
rosebery
Rank: Project Manager
Posts: 2022
Joined: Wed Sep 26, 2007 8:55 pm

Postby greg-s » Sat Feb 14, 2009 7:55 pm

thanks for the advice guys
greg-s
Rank: Labourer
Progress to next rank:
25%
Posts: 2
Joined: Fri Feb 13, 2009 9:13 pm

Postby stoneyboy » Mon Feb 16, 2009 6:15 pm

greg-s,
If you are installing a new spur and cabling different regulations need to be complied with.
end
stoneyboy
Rank: Project Manager
Posts: 2745
Joined: Wed Dec 10, 2008 6:44 pm

Postby kbrownie » Mon Feb 16, 2009 9:57 pm

Hi stoneyboy,
I would be interested to know what different regulations are applied to protecting a spur from mechanical damage?
The regulations regarding addition and extending circuit is a different matter.
A minor works cert is needed
KB
kbrownie
Rank: Project Manager
Posts: 1993
Joined: Mon Mar 05, 2007 9:36 pm

Postby stoneyboy » Tue Feb 17, 2009 9:44 pm

kbrownie,
Sorry my term "different regulations" is a bad choice of words they are after all the same regulations.
Perhaps we should have asked greg-s whether the spur is an addition - if yes then we would have to suggest a more stringent standard of protection or RCD/RCBO fitted on the circuit.
Thanks.
end
stoneyboy
Rank: Project Manager
Posts: 2745
Joined: Wed Dec 10, 2008 6:44 pm

Postby kbrownie » Wed Feb 18, 2009 10:30 am

Hi Stoneyboy,
no worries, just thought I had missed something, earth leakage devices very useful part of systems. May be should have mentioned them in earlier posts.
Was really thinking of mechanical protection rather than shock protection, but good point.
KB
kbrownie
Rank: Project Manager
Posts: 1993
Joined: Mon Mar 05, 2007 9:36 pm

Display posts from previous
Sort by
Order by



  • DIY How to Project Guides

  • DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!



 