possible air lock in gravity HW system
Help and information on all topics relating to your central heating, air conditioning and ventilation issues.

3 posts   •   Page 1 of 1
brookesie
Labourer
Labourer
Posts: 1
Joined: Mon May 25, 2009 9:30 am

possible air lock in gravity HW system

Post by brookesie » Mon May 25, 2009 9:40 am

Anyone have any ideas or suggestions?

We have an old-fashioned conventional gravity fed hot water system, with large (28mm) flow and return pipes coming off the boiler going up into the hot water tank which is in the airing cupboard upstairs. As far as I can tell, there are no valves or pumps, not even a thermostat on the tank. The hot water in the cylinder just heats up when the boiler is on as hot water rises and goes into the primary coil inside the tank, then returns to the boiler.
The problem is that when the boiler is on but the central heating is off ie the room thermostat is turned down, we have no hot water. Only when the heating is on does the hot water in the tank heat up. Previously it would be hot with only the boiler on, ie no rads. There is no way to divert from heating to hot water, ie if boiler is on, then water should be hot.

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 5:22 pm

Post by htg engineer » Mon May 25, 2009 4:21 pm

Gravity Hot Water Sytem - you wont have a tank stat or pump on HW side.

Options to clear airlock:

- I would try this first, Drain system and refill - it might refill properly

- Crack open the 28mm nuts on the tank, hopefully air will escape

- Last resort get an RGI to pull boiler stat - to boil air from the system.

htg

stoneyboy
Project Manager
Project Manager
Posts: 6419
Joined: Wed Dec 10, 2008 6:44 pm

Post by stoneyboy » Mon May 25, 2009 10:24 pm

brookesie,
There is the possibilty that the gravity feed pipes are clogged, the only way to tell is to drain the system and open up a joint on these pipes.
end

3 posts   •   Page 1 of 1