Postby armytouch » Thu May 15, 2008 8:46 pm

Hi, Had electric shower installed, 10mm cable from shower to 45a isolator switch then a direct feed 2.5mm cable to consumer unit a nsb40a circuit breaker on fitted to RCD side of unit. Was working great but then 40a breaker tripped.when put it back on isolator switch on but shower wont turn on.
Any ideas?
armytouch
Rank: Ganger
Progress to next rank:
18%
Posts: 77
Joined: Mon Jan 14, 2008 1:49 am

Sponsor

Simply Build It

Postby ericmark » Fri May 16, 2008 9:07 am

2.5mm² cable from isolator to consumer unit is far too small. 2.5mm² even clipped direct to metal tray to remove the heat can only take 27 amps that 6.2Kw and I have never seen a shower that small. In an insulated wall it is only ratted at 13.5 amp thats 3.1Kw it would act more like a fuse wire and I would turn the power off and rewire ASAP.
ericmark

Postby armytouch » Fri May 16, 2008 1:51 pm

Sorry but cabling is all 6mm,from shower through isolation to consumer unit.
armytouch
Rank: Ganger
Progress to next rank:
18%
Posts: 77
Joined: Mon Jan 14, 2008 1:49 am

Postby ericmark » Fri May 16, 2008 9:48 pm

That's a little better 6mm² is rated at about 35amp or 8Kw and 40amp is 9.2Kw you do not say what size the shower is really should be 8Kw or less. The larger MCB are getting very near to max for the size of breaker and if overloaded do sometimes fail. Sometimes they look as if they have reset but haven't is there a neon on the isolator and if so is it lit. Which what you tell us there is very little we can do to help really does need site visit to sort out this sort of fault. Do you know shower size?
ericmark

Postby armytouch » Sat May 17, 2008 9:47 am

Hi,the shower is 8.5kw,6mm cable running straight thru to isolator with neon,then 6mm cable running direct to 40a breaker in consumer unit,loose cable tripped breaker,reconnected and all seems fine now,cheers
armytouch
Rank: Ganger
Progress to next rank:
18%
Posts: 77
Joined: Mon Jan 14, 2008 1:49 am

Display posts from previous
Sort by
Order by



  • DIY How to Project Guides

  • DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!



 