Too many sockets over too large area for protective device.


Postby I_spark » Tue Aug 07, 2007 7:56 pm

Hello,
The circuit is Sockets down 2.5/1.5 cable 8 points served (No ring) 15 A Bs 3036.
How can this problem be solved and rectified?

For sockets up again no ring 30 A BS 3036 2.5/1.5 3 points served it says too large protective device for cable size. How can this be solved and rectified?

Thanks in advance.
I_spark
Posts: 8
Joined: Thu Jul 12, 2007 9:15 am

Sponsor

Simply Build It

Postby BLAKEY1963 » Tue Aug 07, 2007 9:13 pm

[quote="I_spark"]Hello,
The circuit is Sockets down 2.5/1.5 cable 8 points served (No ring) 15 A Bs 3036.
How can this problem be solved and rectified?

For sockets up again no ring 30 A BS 3036 2.5/1.5 3 points served it says too large protective device for cable size. How can this be solved and rectified?

Thanks in advance.[/quote]

I SPARK
2.5 MM2 AS A RADIAL CIRCUIT CAN SERVE A FLOOR SPACE NOT EXCEEDING 50 M2 IF PROTECTED BY A 20 AMP PROTECTIVE DEVICE . TYPE OF CIRCUIT IS A2 FROM OSG PAGE 151
BLAKEY1963
Posts: 654
Joined: Wed Jun 13, 2007 10:57 pm