utilities access to new house

Postby painter 1 » Mon Feb 18, 2008 1:08 pm

Can all utilities ( Gas, Electric ,Water,phone )be run in the same trench for access into house ,if not how far apart would the recomendation be.
painter 1
Rank: Labourer
Progress to next rank:
Posts: 1
Joined: Mon Feb 18, 2008 12:56 pm


Simply Build It

Postby kbrownie » Sat Feb 23, 2008 10:33 am

Hi painter 1.
I believe they can be routed in same trench, they may have to be at different levels, the electric cables and data cables should be seperated. (not bunched together) but same trench I think the regs should be 150mm a part. But don't take it as gospel!
Rank: Project Manager
Posts: 1759
Joined: Mon Mar 05, 2007 9:36 pm

Postby matt h » Fri Mar 28, 2008 2:15 am

they can all be in the same trench, with the water lowest at about 900mm with 150mm between layers and the electric supply in ducts. Where they enter building must be in sleeve duct sealed against rodent entry.
matt h
Rank: Tradesman
Progress to next rank:
Posts: 24
Joined: Thu Mar 27, 2008 11:35 pm

Display posts from previous
Sort by
Order by

  • DIY How to Project Guides

  • DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!