I have posted similar a couple of weeks ago. I had major problems in trying to remove air from the central heating. I have to have the pump at level 3 to reduce the noise (banging) of air in the system. I got a plumber in, who drained down the system a couple of times before it was reasonable. Less air in the sytem, but still banging in the pipes when I reduce the pump speed to 2, so not solved completely.
The plumber blew into the vent pipe to try and finally remove the air . Can someone tell me what this actually does? I can see that it might move an air lock, but will it also push further air into the sytem?
If the pipework layout is causing airlocks when filling from the F&E tank try filling the system from the other way ie bottom up. Drain system again, ensure all bleed valves on rads are closed, put your hosepipe on the drain valve (secure it with jubilee clip), open up your mains supply and let it go. Its advisable to have two people for this job. One in the roof to monitor the arrival of water in the F&E tank to know when to shut supply off and the other to stick by the hose to drain valve connection in case they part company during the process. Once you have the pipework filled you can open up the bleed valves one by one and let water back into your rads.
DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!