air in pipe after pump

by jim barlow » Fri Apr 18, 2008 2:30 pm

I have cleaned and flushed system but on refilling I cannot get a flow to the radiators, the hot water system is fine, I have fitted anew pump and zone valve all points have been bled but I cannot get a flow to the radiators. Please HELP. Jim Barlow

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 6:22 pm

by htg engineer » Fri Apr 18, 2008 8:14 pm

Vented all air from pump vent ? turned pump speed to maximum ?

Are you sure the zon valve or three port valve ? fitted correctly and working ?

room stat calling for heat ?

Select hot water, remove actuator and trun the valve manually - if the radiators heat it's the actuator at fault.