Hi guys,
Ariston eurocombi A/23. DHW intermittent. Heating fine. Pressure was at 3 bar. Lowered to 1. Boiler now comes on for longer when on demand for hot water, but can hear a clicking from around the gas valve (solenoid maybe ?) Turn hot tap off, boiler runs continously with no demand on for heating or DHW and rads warm up.
The only way to stop boiler running is to switch off at the boiler on/off switch. Never come across this one yet.
Cmon htg engineer & co help me out here boys.
Have you check that the DHW flow switch and CH and/or DHW microswitches aren't sticking ?
If the DHW microswitch or flow switch is sticking then the boiler will stay on, with there being no hot water demand the heat is finding it's way to the radiators.
Why was the pressure at 3 bar ?
It's either:
been topped up too much ? <<<<<<same as rosebery states below.
plate heat-ex leaking ?
expansion vessel not taking up the expansion?
htg
Last edited by htg engineer on Sat Jul 11, 2009 5:06 pm, edited 1 time in total.
cheers htg eng. your a god send. can always rely on you dude, and thanks also rosebery. was 3 bar when i arrived. filling loop slightly open. Will look at what youve suggested.
DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!