footings for cony

by vibetime » Tue Nov 02, 2010 4:50 pm

hi all,
is it viable to concrete over a plastic drain pipe spanning the width of my trench ?
have same problem with electric cable duct in two places also ?
moving is not an option really to either as involves masses of extra labour
i want to trench fill so cant bridge with lintels either.
been told to wrap in insulation and just pour away , but can it be reinforced around the ducts/pipe with steel mesh somehow ?
thanks for any help

welsh brickie
Project Manager
Project Manager
Posts: 2610
Joined: Sat Apr 12, 2008 8:54 am

foundation

by welsh brickie » Tue Nov 02, 2010 6:16 pm

you must have concrete under the pipe excavate a trench under the pipe 450mm under the pipe and encase the pipe in concrete if the pipe is visible above the concrete once its laid you must bridge it with a lintol.As for the electric cable ducting you can just concrete over it,the ducting will protect the cable

vibetime
Apprentice
Apprentice
Posts: 12
Joined: Mon Oct 25, 2010 10:52 pm

by vibetime » Wed Nov 03, 2010 6:13 pm

thanks welsh brickie, spoke to building inspector and this issue is sorted.