I've recently had a new boiler installed - Potterton Suprima HE.
I also have a new programmer - Honeywell ST699 and Room stat - Honeywell DT90E.
The Programmer is a Sundial Y plan with a gravity hot water/pumped central heating system so the heating only works when the water is also on.
The hot water works fine on it's own.
When i have the heating on it fires up ok but when it stops firing, both the water and heating power lights flash on and off simultaneously.
Hi
could it be anything to do with the room stat?
the old honeywell one i removed had a 3 wire connection. The new one - DT90E is using only 2 wires ie without the neutral.
When the neutral is connected it trips the RCD.....
cronky wrote:The Programmer is a Sundial Y plan with a gravity hot water/pumped central heating system so the heating only works when the water is also on.
Do you not mean "C" plan? The "Y" plan is fully pumped with a 3 port valve.
cronky wrote:..............both the water and heating power lights flash on and off simultaneously.
Do the lights continually pulse on and off? If so the programmer unit may be set incorrectly. Check the handbook.
cronky wrote:When the neutral is connected it trips the RCD.....
The neutral must not be used on a two wire stat. Connecting it may damage the unit!
DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!