IP65 STEPPED EDGE DIE CAST BATHROOM SHOWER LIGHT

by nick119 » Thu Nov 13, 2008 8:35 pm

Hi i have just bought 10 IP65 STEPPED EDGE DIE CAST BATHROOM SHOWER LIGHTS and would like to know what terminal/connector box could use to connect these all from the same supply they all have there own transformer which is an OE 60T UK ? Thanks

ericmark

by ericmark » Fri Nov 14, 2008 2:12 am

Although simply adding up the current on each lamp you should be OK in practice the inrush for so many lights will trip out a 6 amp MCB so you will need at least two switches. Hager do some special junction boxes which do not require access once complete because of the spring clip arrangement but most JBs will need access for maintenance.
If in a shower or bathroom they will come under Part P and will now need RCD protection.
Eric