Low pressure fault - Flexcom boiler
Help and information on all topics relating to your central heating, air conditioning and ventilation issues.

2 posts   •   Page 1 of 1
Soccy
Labourer
Labourer
Posts: 1
Joined: Sun Sep 19, 2021 12:34 pm

Low pressure fault - Flexcom boiler

by Soccy » Sun Sep 19, 2021 12:40 pm

Hi, occasionally get a low pressure fault on ce natural heating system (f&e) in loft. No signs of any leaks plus no recent bleeding of radiators. Any suggestions bar topping up f&e tank noting I thought ballcock valve would refill automatically as free moving?
Boiler serviced annually with no issues raised,
Thanks in advance,

stoneyboy
Project Manager
Project Manager
Posts: 6429
Joined: Wed Dec 10, 2008 6:44 pm

Re: Low pressure fault - Flexcom boiler

by stoneyboy » Tue Sep 21, 2021 10:44 pm

Hi soccy
Suggest you look up the minimum operating pressure for you boiler. If it’s being fed by a tank in the loft you will be getting less than 1bar.
Regards S