No Heating since new pump fitted
All aspects of plumbing questions and answers, help, tips and information

5 posts   •   Page 1 of 1
adman_lincoln
Labourer
Labourer
Posts: 2
Joined: Sun Mar 01, 2009 11:42 am

No Heating since new pump fitted

Post by adman_lincoln » Sun Mar 01, 2009 11:49 am

Hi I have just fitted a new circulating pump and now the boiler only fires for a few mins.

I have made sure I have fitted it the right way followed venting procedures and bled the radiators.

The pump works but the hot water only seems to get to the 3 way valve then the boiler gives up. The position on the valve moves when switched between water and heating and it worked fine before pump replacement.

The reason for replacing was noise.

Any help with this would amazing.

Thanks

plumbbob
Project Manager
Project Manager
Posts: 1892
Joined: Wed May 07, 2008 9:59 pm

Post by plumbbob » Sun Mar 01, 2009 2:55 pm

The logical explanation is you still have air trapped in the pipework which is preventing the flow. Either crack a joint open to let out water and the air plug, or consider popping the pump in backwards temporarily to shift it.

tomkev1
Labourer
Labourer
Posts: 3
Joined: Tue Mar 03, 2009 10:01 am

Post by tomkev1 » Tue Mar 03, 2009 11:23 am

IT is well worth checking that you have fully opened the pump valves and not closed them.I.E that is open them in the same direction as you would a normal tap.I once had a plumber/gasman workmate of mine make the same simple mistake, took him ages to find the fault.

:oops:

[/u]

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 5:22 pm

Post by htg engineer » Tue Mar 03, 2009 4:58 pm

Try venting the pump.


htg

adman_lincoln
Labourer
Labourer
Posts: 2
Joined: Sun Mar 01, 2009 11:42 am

Post by adman_lincoln » Tue Mar 03, 2009 7:03 pm

Hi thanks it turns out I'm all bunged up with slugde!!! So now in the process of flushing the system. Either that or pay £500 to a plumber!

5 posts   •   Page 1 of 1
It is currently Tue Apr 09, 2024 1:24 pm