I'm adding a socket to an existing ring protected by a 32a mcb with a mixture of white 7 strand t+e and grey 2.5mm t+e cabling.
Just want to check that it is ok to use 2.5mm t+e rated at 27a when the circuit is protected by a 32a mcb??? Assume it is as it already used in the curcuit?
Also, am I right in thinking adding a bedroom socket to an existing ring doesn't require a part p "competent person"?
hi AIDO right both times,
although 2.5 rated lower than 32A, this is the reason you are only allowed one double skt as a max on unfused spur from ring 'cos even if both outlets fully loaded max current in spur would be 2 X 13A = 26A because of fuses limiting effect.
Yes You can add a spur to ring as long as not in kitchen!
regards SPARX
DIY how to tutorial projects and guides - Did you know we have a DIY Projects section? Well, if no, then we certainly do! Within this area of our site have literally hundreds of how-to guides and tutorials that cover a huge range of home improvement tasks. Each page also comes with pictures and a video to make completing those jobs even easier!