ventilation......YES/NO

by vw754 » Thu Apr 10, 2008 5:58 pm

IM HAVINA A new boiler/pipes/rads. The original boiler was behind the fire in the lounge,which has now been taken out,im also going to buy a new gas fire as im renovating,will the ventilation still be needed or is it best to leave it be ?

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 6:22 pm

by htg engineer » Sat Apr 12, 2008 10:05 pm

A gas fire with a heat input of 7kw or less does not rquire ventilsation.

A gas fire with a heat input of 7kw or more does require ventilation and a DFE gas fire required 100cm2 ventilation.

A combi boiler does not require combustion ventilation - but some manufacturers do specify having cooling vents.