Very old wiring in ceiling rose help needed installing bathroom light
Ask questions and find answers to many subjects relating to electrics and electrical work

3 posts   •   Page 1 of 1
cazzalaw
Labourer
Labourer
Posts: 3
Joined: Sat Jan 21, 2017 10:20 am

Very old wiring in ceiling rose help needed installing bathroom light

Post by cazzalaw » Sat Jan 21, 2017 10:56 am

I want to install a new bathroom light. The new light has got three 6.3W bulbs. It will be the only light in the bathroom and is operated by a pull string.

The wiring is very old in this Victorian property.

There are two red and two black wires coming out of the ceiling. I have already successfully "plumbed" a light fitting which works fine but the fitting on my new light is slightly different and I'm wondering how to feed the red and black wires into it.

The existing light fitting is set up like this
IMG_8295.jpg



The new fitting looks like this
IMG_8296.jpg



The picture of the new light fitting hasn't come out too well but basically there are only Two "inlets" per N / symbol / L, unlike the previous set up which had a greater number of "inlets".

Please could someone explain where I should put the black and red wires into the new fittings' inlets.

Thanks in advance,
You do not have the required permissions to view the files attached to this post.

ericmark
Project Manager
Project Manager
Posts: 2853
Joined: Fri Oct 02, 2009 8:49 pm
Location: Llanfair Caereinion, Mid Wales.

Re: Very old wiring in ceiling rose help needed installing bathroom light

Post by ericmark » Mon Jan 23, 2017 2:37 am

Looking at pictures it would seem simple answer is you can't use that lamp. In 1966 the rules on lighting changed, before 1966 there was no need to have an earth in lighting circuits, the introduction of metal light fitting specially fluorescent changed the rules.

Today one can still use the old system, there is no law saying you must up grade, however any light fitting used must be class II in other words designed to work with no earth.

I had this with mothers house, and I decided I may need to rent out her house, so cure was a re-wire so I could if required rent out her house. Before this I wanted lights for the kitchen, I paid some thing like £80 for a lamp which looked exactly the same as one costing £30 in B&Q just so it had the double square sticker saying it was class II.

The house had metal wall lights, fitted before 1966, which to my mind were too easy to put a hand on when putting coats on the coat hangers in the hall. And also an attempt to fit a consumer unit with RCD protection had failed, the RCD was forever tripping, so clearly there were wiring problems some where. So the re-wire gave me piece of mind.

Apart form the earth he wiring problem you have is common, we wire ceiling rose to ceiling rose which drops from ceiling rose to switch, this gives both advantages and disadvantages, easy to wire a ceiling fan or emergency lights, but there is no neutral in the light switch so there are also some down side bits. So we have an extra terminal in our ceiling roses, we have a permanent line as well as switched line.

Some times it's a simple case of swapping a three section connector block for a four section block to give extra terminal, other times using a junction box, there are some made specially for the job. Hager J501 is a good example of a lighting junction box which converts UK type wiring into EU type wiring used a lot for fitting down lights. The J804 is maintenance free, for use where only access would be to lift floor boards.

However in your case since you have no earth, these will not allow you to fit the lamp you have, you need a re-wire first. Also one of those black wires should have a red sleeve on it to show it's switched line not neutral.

So connecting the two reds together with a connector block and putting the two blacks one to line (L) the other to neutral (N) would make the light work, but without the earth wire it would not be safe, and since you don't know which of the two blacks is neutral and which is switched line you can't use any screw type bulbs, as the thread has to be neutral and you don't know which is which.

It also means you can't used metal light switches, and you need little plastic bungs to cover the screw heads for screws holding the switches in place, or plastic screws, or plastic back boxes. You could put a blob of silicon sealant on each screw, that would also stop anyone touching the retaining screws.

cazzalaw
Labourer
Labourer
Posts: 3
Joined: Sat Jan 21, 2017 10:20 am

Re: Very old wiring in ceiling rose help needed installing bathroom light

Post by cazzalaw » Mon Jan 30, 2017 2:53 pm

Wow!

Thank you so much for such comprehensive information and advice - it is so helpful and I'm sure will be useful for others too.

It seems apparent to me that I will not be able to use the new light fitting which I wanted to use as it's metal! I'm so glad you pointed that restriction out to me - thank you